ISO9001 H a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e Marine & Offshore Cable www.lscable.com

[close]

p. 2

The enterprise that is together with human beings through the information and energy transmission technology NEK606 Type Cable H a l o g e n f r e e a n d M u d R e s i s t a n t C a b l e Leading the World out of sight For affluent and convenient life of human beings, LG Cable connects the human mind and transmits the light and energy out of sight such as industrial sites, offices, home, and various instruments that we use. In order to realize the dream of "the world that is connected by the light and that we grow up with energy", all the technologies of LG Cable are based on human beings and environment. The technology that makes the human life rich and protects and harmonizes the environment is the dream that LG Cable pursues. LG Cable moves the world in every world in silence. corner of the Index Reference Standards Safety-related Instruction Cable Designation Index of symbols General Requirements Electrical Properties Mechanical Properties Cable Construction Details Technical Information Other Productions Quality Assurance Program H a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 3 Marine & Offshore Cable

[close]

p. 3

Safety-related Instruction The following safety-related instructions are to help you use products safely and precisely, and to prevent unexpected danger or damage. According to the extent of risk, damage and emergency of risk occurrence anticipated when products are incorrectly used, the safety-related instructions are classified as follows; , , . , . Warning Caution In case of using products incorrectly by ignoring this indication, it is possible to anticipate mortality risks or severe wounds. ( , .) In case of using products incorrectly by ignoring this indication, it is possible to anticipate slight wounds or property damage. ( , .) Warning It may be the cause of a fire or damage by a fire. ( , Do not use in excess of a rated voltage and an allowable current. ( , .) .) .) REFERENCE STANDARDS NEK606 IEC60228 IEC60092-350 IEC60092-351 IEC60092-353 IEC60092-354 IEC60092-359 IEC60092-375 IEC60331 IEC60332-1 IEC60332-3 IEC60502 IEC60754 IEC60811 IEC61034 CSAC22.2No.38 Cables for offshore installations Halogen Free, or Mud Resistant Conductors of insulated cables Shipboard power cables - General construction and test requirements Insulation materials for shipboard cables Single and multicore non-radial field power cables with extruded solid insulation for rated voltages 1kV and 3kV Single and three-core power cables with extruded solid insulation for rated voltages 6kV, 10kV and 15kV Sheathing materials for shipboard cables Shipboard telecommunication cables and radio-frequency cables Test for electric cables under fire conditions Tests on electric cables under fire conditions Tests on electric cables under fire conditions (Cat.A,A/F) Extruded solid dielectric insulated power cables for rated voltages from 1KV up to 30KV Test on gases evolved during combustion of electric cables Common test methods for insulating and sheathing materials. Measurement of smoke density of electrical cables burning under designed conditions Cold impact & Cold bending test for wires or cables R:Radius of curvature T:Pulling tension It may be the cause of an electric shock.( Do not conduct connection operations when power is on. ( .) , It may be the cause of a fire or an electric shock.( Do not disassemble or convert products. ( , .) .) It may be the cause of a fire or damage by a fire.( , .) Keep heat-resisting temperature of cable, considering the environment of using. ( .) Be sure to earth an screened products. ( .) Caution Cable is not untied.( Pile up drums after making them stand. ( .) .) It may be the cause of damage to a cable.( .) When you hang a drum on the crane, keep sufficient length to the extent that an angle of the wire can be under 60 degree. ( ( ( , .) .) 60 .) It may be the cause of disconnection or breakdown of a cable. Keep the permissible pulling tension and radius of bend. It may be the cause of damage to a cable.( .) Do not drop a drum.( .) Use an A-frame carrier or a crane.( .) It may be the cause of damage to a cable.( .) In case of processing the terminal of cable, keep water from percolating. ( .) .) It may be the cause of damage to a cable.( Do not use except its fixed purpose according to each kind of cable. ( .) Before using products, read these instructions. ( .) Use products after verifying indefinite details besides the above descriptions from our company. ( ( .) .) Keep this safety-related instructions in the place it can always be seen by users after reading it. H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 4 5 Marine & Offshore Cable

[close]

p. 4

Cable Designation Symbol 3.6/6KV RFOU 3.6/6KV RFCU 3.6/6KV RFOB 3.6/6KV RFCB 3.6/6KV BFOU 3.6/6KV BFCU 3.6/6KV BFOB 3.6/6KV BFCB 6/10KV RFOU 6/10KV RFCU 6/10KV RFOB 6/10KV RFCB 6/10KV BFOU 6/10KV BFCU 6/10KV BFOB 6/10KV BFCB 8.7/15KV RFOU 8.7/15KV RFCU 8.7/15KV RFOB 8.7/15KV RFCB 8.7/15KV BFOU Max. Temp.( ) 85 85 85 85 85 85 85 85 85 85 85 85 85 85 85 85 85 85 85 85 85 Type of Cable 3.6/6KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 3.6/6KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 3.6/6KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 3.6/KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 3.6/6KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 3.6/6KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 3.6/6KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering tinned copper wire braid armored and SE1 sheathed cable 3.6/6KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 6/10KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 6/10KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 6/10KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 6/10KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering galvanized steel wire braid armored and SE1 sheathed cable 6/10KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 6/10KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 6/10KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 6/10KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 8.7/15KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 8.7/15KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 8.7/15KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 8.7/15KV EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 8.7/15KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable Page 14 14 14 14 17 17 17 17 15 15 15 15 18 18 Symbol 8.7/15KV BFCU 8.7/15KV BFOB 8.7/15KV BFCB 0.6/1KV RFOU 0.6/1KV RFCU 0.6/1KV RFOB 0.6/1KV RFCB 0.6/1KV BFOU 0.6/1KV BFCU 0.6/1KV BFOB 0.6/1KV BFCB 250V RFOU(c) 250V RFCU(c) Max. Temp.( ) 85 85 85 85 85 85 85 85 85 85 85 85 85 Type of Cable 8.7/15KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 8.7/15KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cables 8.7/15KV Mica tape, EPR insulated, Tinned cu tape or tinned copper wire shield, halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 0.6/1KV EPR insulated, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 0.6/1KV EPR insulated, halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 0.6/1KV EPR insulated, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 0.6/1KV EPR insulated, halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 0.6/1KV Mica tape, EPR insulated,halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 0.6/1KV Mica tape, EPR insulated, halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 0.6/1KV Mica tape, EPR insulated, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 0.6/1KV Mica tape, EPR insulated, halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape collective screen, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape collective screen, halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape collective screen, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape collective screen, halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 250V Mica tape, EPR insulated, copper/polyester tape or aluminum/polyester tape collective screen, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 250V Mica tape, EPR insulated, copper/polyester tape or aluminum/polyester tape collective screen,halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 250V Mica tape EPR insulated, copper/polyester tape or aluminum/polyester tape collective screen, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 250V MIca tape EPR insulated, copper/polyester tape or aluminum/polyester tape collective screen, halogen free covering, galvanized steel wire braid armored and SE1 sheathed cable Page 19 19 19 20 20 20 20 24 24 24 24 28 28 250V RFOB(c) 85 85 85 28 28 30 18 250V RFCB(c) 18 250V BFOU(c) 16 16 16 16 250V BFCB(c) 250V BFCU(c) 85 30 250V BFOB(c) 85 30 85 30 19 H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 6 7 Marine & Offshore Cable

[close]

p. 5

Symbol 250V RFOU(i) 250V RFCU(i) Max. Temp.( ) 85 85 Type of Cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape individual screen, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape individual screen, halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape individual screen, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape individual screen, halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 250V Mica tape, EPR insulated, copper/polyester tape or aluminum/polyester tape individual screen, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 250V Mica tape, EPR insulated, copper/polyester tape or aluminum/polyester tape individual screen,halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 250V Mica tape EPR insulated,copper/polyester tape or aluminum/polyester tape individual screen, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 250V Mica tape EPR insulated, copper/polyester tape or aluminum/polyester tape individual screen,halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape individual and collective screen, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape individual and collective screen,halogen free inner covering, galvanized steel wire braid armored and SHF2 sheathed cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape individual and collective screen, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 250V EPR insulated, copper/polyester tape or aluminum/polyester tape individual and collective screen, halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 250V MIca tape, EPR insulated, copper/polyester tape or aluminum/polyester tape individual and collective screen, halogen free inner covering, tinned copper wire braid armored and SHF2 sheathed cable 250V Mica tape, EPR insulated, copper/polyester tape or aluminum/polyester tape individual and collective screen, halogen free inner covering,galvanized steel wire braid armored and SHF2 sheathed cable 250V Mica tape EPR insulated, copper/polyester tape or aluminum/polyester tape individual and collective screen, halogen free inner covering, tinned copper wire braid armored and SE1 sheathed cable 250V Mica tape EPR insulated, copper/polyester tape or aluminum/polyester tape individual and collective screen, halogen free inner covering, galvanized steel wire braid armored and SE1 sheathed cable 0.6/1 KV EPR insulated and SHF2 sheathed cable 0.6/1KV EPR insulated and SE1 sheathed cable 0.6/1KV SHF2 insulated cable Page 32 32 Index of symbols 250V RFOB(i) 250V RFCB(i) 250V BFOU(i) 85 85 85 32 32 34 250V BFCU(i) 85 34 250V BFOB(i) 85 34 250V BFCB(i) 85 34 Letter 36 Meaning Flame retardant cables Fire resistant & Flame retardant cables Halogen free thermoset compound Bedding or taping Tinned copper wire braid Galvanized steel wire braid No armor Halogen free thermoset compound Mud resistant type Individual screen Collective screen Individual & collective screen Remark IEC60332-3 Cat.A IEC60331 & IEC60332-3 Cat.A IEC60092-359 SHF2 250V RFOU(i/c) 85 R 1st B U F O C X U 4th B (i) 5th (c) (i/c) 250V RFCU(i/c) 85 36 2nd 3rd 250V RFOB(i/c) 85 36 250V RFCB(i/c) 85 36 IEC60092-359 SHF2 IEC60092-359 SE1 Copper/polyester or Aluminum/polyester with drain wire Copper/polyester or Aluminum/polyester with drain wire Copper/polyester or Aluminum/polyester with drain wire 250V BFOU(i/c) 85 38 250V BFCU(i/c) 85 38 250V BFOB(i/c) 85 38 250V BFCB(i/c) 85 38 0.6/1KV RU 0.6/1KV RB 0.6/1KV RX 0.6/1KV UX 85 85 85 40 40 44 H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 8 9 Marine & Offshore Cable

[close]

p. 6

General Requirements Flame retardant(for completed cable) The cables shall withstand the test specified in IEC60332-3 Cat.A or A/F. Fire resistant(for fire resistant type completed cable) Fire resistant cables shall be tested according to IEC60331. Content of halogen(for inner covering & sheath) As a rule, all cables shall be halogen free according to IEC60754-1,maximum content of halogen=5mg/g. For mud resistant cables, a halogen content necessary to achieve diesel based mud resistant,will be acceptable. Smoke emission(for completed cable) When tested according to IEC61034-2, smoke emission shall be kept to minimum 60% transmittance. Oil resistant(for outer sheath) All thermoset sheathed cables shall be suitable for an oil production installation. The oil resistant properties shall demonstrated by a test according to IEC6092-359 Table 2 clause 3. Mud resistant Mud resistant cables shall be designed with sheathing compounds suitable for installation and operation on contact with Mud unless otherwise specified. The mud resistant properties shall be demonstrated by the following test procedure; The cables shall be immersed in Mud at 70 , and tested for changes of elongation at break, tensile strength, volume swelling, weight increase and oxygen index after 56 days. Requirements : - Elongation at break - Tensile strength - Volume swelling - Weight increase - Oxygen index Max. Max. 25% 25% Electrical Properties For 3.6/6 KV cables Conductor Size SQMM 25 35 50 70 95 120 150 185 240 300 Conductor Resistance (20 ) Ohm/km 0.734 0.529 0.391 0.27 0.195 0.154 0.126 0.1 0.0762 0.0607 Insulation Resistance (20 ) (85 ) Mohm-km 1100 900 800 700 600 550 500 450 400 350 1.1 0.9 0.8 0.7 0.6 0.6 0.5 0.5 0.4 0.4 Test Voltage KV/5min 11 11 11 11 11 11 11 11 11 11 For 6/10 KV cables Conductor Size SQMM 25 35 50 70 95 120 150 185 240 300 Conductor Resistance (20 ) Ohm/km 0.734 0.529 0.391 0.27 0.195 0.154 0.126 0.1 0.0762 0.0607 Insulation Resistance (20 ) (85 ) Mohm-km 1100 1000 900 800 700 600 550 500 450 400 1.1 1.0 0.9 0.8 0.7 0.6 0.6 0.5 0.5 0.4 Test Voltage KV/5min 15 15 15 15 15 15 15 15 15 15 For 8.7/15 KV cables Conductor Size SQMM 25 35 50 70 95 120 150 185 240 300 Conductor Resistance (20 ) Ohm/km 0.734 0.529 0.391 0.27 0.195 0.154 0.126 0.1 0.0762 0.0607 Insulation Resistance (85 ) (20 ) Mohm-km 1400 1200 1100 950 850 750 700 650 550 500 1.4 1.2 1.1 1.0 0.9 0.8 0.7 0.7 0.6 0.5 Test Voltage KV/5min 22 22 22 22 22 22 22 22 22 22 Max. 20% Max. 15% Min. 25% Cold Resistant Test method and requirements shall comply with CSA C22.2 No.38. For 250V cables Conductor Size SQMM 0.75 1 1.5 Conductor Resistance (20 ) Ohm/km 26.0 18.2 12.2 Insulation Resistance (85 ) (20 ) Mohm-km 1400 1250 1100 1.4 1.3 1.1 Test Voltage KV/5min 1.5 1.5 1.5 H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 10 11 Marine & Offshore Cable

[close]

p. 7

For 0.6/1KV cables Conductor Size SQMM 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 Mechanical Properties of SHF2 Conductor Resistance (20 ) Ohm/km 12.2 7.56 4.7 3.11 1.84 1.16 0.734 0.529 0.391 0.27 0.195 0.154 0.126 0.1 0.0762 0.0607 Insulation Resistance Note) (20 ) Mohm-km 1300 1100 900 800 700 600 500 450 450 450 400 350 350 350 350 350 (85 ) 1.3 1.1 0.9 0.8 0.7 0.6 0.5 0.5 0.5 0.5 0.4 0.4 0.4 0.4 0.4 0.4 Test Voltage KV/5min 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 3.5 Applicable standard:IEC 60092-359 Description Maximum rated conductor temperature for normal operation A. Without aging 1. Tensile strength 2. Elongation at rupture B. After aging in air oven (120 2 /168hrs) 1. The variation of Tensile strength 2. The variation of Elongation at rupture C. After immersion in hot oil (100 2 /24hrs) 1. The variation of Tensile strength 2. The variation of Elongation at rupture D. Compatibility test (95 2 /168hrs) 1. The variation of Tensile strength 2. The variation of Elongation at rupture E. Hot set test (200 3 /15min.,20N/cm2) 1. Permissible elongation 2. Permanent elongation F. Cold resistant characteristics 1. Bending(Insulation dia: not more than 12.5mm) (-15 /16hr) 2. Elongation test(Insulation dia: not more than 12.5mm) (-15 /4hr) 3. Impact test (-15 /16hr) G. Ozone resistance (0.025-0.03%ozone,25 2 /24hrs) N/mm2 % % % % % % % % % % Unit SHF2 85 Min. 9.0 Min. 120 70~130 70~130 60~140 60~140 70~130 70~130 Max.175 Max.25 No crack Min. 20 No crack No crack Note) For UX, RX cables, this shall not be considered. Mechanical Properties of EPR Applicable standard : IEC60092-351 Description Maximum rated conductor temperature for normal operation A. Without aging 1. Tensile strength 2. Elongation at rupture B. After aging in air oven (135 3 /168hrs) 1. The variation of Tensile strength 2. The variation of Elongation at rupture C. Characteristics of aging resistance in pressurized air (127 1 /40hrs, 0.55Mpa) 1. The variation of Tensile strength 2. The variation of Elongation at rupture D. Compatibility test (95 2 /168hrs) 1. The variation of Tensile strength 2. The variation of Elongation at rupture E. Voltage test for 4hr F. Constant for insulation resistance at 85 (high temperature) G. Ozone resistance(0.025-0.03%ozone/30hr) H. Electrical capacitance characteristics (lmmersion in warm water at 50 ) 1. Increase between 1st day and 14st day 2. Increase between 7st day and 14st day I. Hot set test(250 3 /15min.,20N/cm ) 1. Permissible elongation 2. Permanent elongation 2 Unit EPR 85 N/mm2 % Min. 4.2 Min. 200 Mechanical Properties of SE1 Applicable standard:IEC 60092-359 Description Maximum rated conductor temperature for normal operation A. Without aging 1. Tensile strength 2. Elongation at rupture B. After aging in air oven (100 2 /168hrs) 1. The variation of Tensile strength 2. Elongation at rupture 3. The variation of Elongation at rupture C. After immersion in hot oil (100 2 /24hrs) 1. The variation of Tensile strength 2. The variation of Elongation at rupture D. Compatibility test (95 2 /168hrs) 1. The variation of Tensile strength 2. Elongation at rupture 3. The variation of Elongation at rupture E. Hot set test (200 3 /15min., 20N/cm2 ) 1. Permissible elongation 2. Permanent elongation F. Ozone resistance (0.025-0.03%ozone, 25 2 /24hrs) % % 70~130 70~130 Unit SE1 85 % % 70~130 70~130 N/mm2 % Min. 10.0 Min. 300 % % - 70~130 70~130 To withstand Min. 3.67 No crack % % % 70~130 Min. 250 60~140 % % 60~140 60~140 % % Max. 15 Max. 5 % % % 70~130 Min. 250 60~140 % % Max. 175 Max. 15 % % - Max.175 Max.15 No crack H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 12 13 Marine & Offshore Cable

[close]

p. 8

R F O U RFCU RFOB RFCB NEK606 Type Cable Voltage rating - 3.6/6KV, 6/10KV, 8.7/15KV Table 2 : 3.6/6KV, 3CORE Conductor Size mm2 25 35 50 70 95 120 150 Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 Inner covering thickness mm 1.4 1.4 1.4 1.6 1.6 1.6 1.6 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 mm 3.0 3.0 3.0 3.0 3.0 3.0 3.0 Diameter over inner covering mm 41.4 44.0 45.9 50.0 54.7 59.0 61.0 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 3700 4230 4880 5990 7270 8500 9730 mm 2.6 2.7 2.7 2.9 3.1 3.3 3.4 mm 49.0 52.0 54.0 58.7 63.5 68.0 71.0 mm 3.0 3.1 3.3 3.5 3.5 3.7 3.7 Maximum conductor temperature - 85 Applied Standards - IEC 60092-354 - NEK 606 - IEC 60332-3 Cat. AF - IEC 60754-1 & 2 - IEC 61034-2 Table 3 : 3.6/6KV, 3+E CORE Conductor Size mm2 25 35 50 70 95 120 150 Construction Details - Conductor IEC 60228 Class 2 - Conductor Screen Semi-conducting compound - Insulation HF-EPR as per IEC 60092-351 - Insulation Screen Semi-conducting compound - Metallic Screen Tinned copper wire braid or Tinned Copper tape - Inner covering Halogen-free compound - Armor Tinned copper wire braid - Sheath IEC 60092-359, SHF2 Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 Inner covering thickness mm 1.4 1.4 1.4 1.6 1.6 1.6 1.6 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 mm 3.0 3.0 3.0 3.0 3.0 3.0 3.0 Diameter over inner covering mm 41.4 44.0 46.4 50.9 56.4 60.9 62.9 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 4500 5150 6050 7400 9130 10500 12320 mm 2.6 2.7 2.8 2.9 3.2 3.3 3.4 mm 49.7 52.5 55.0 60.0 66.0 70.8 73.0 mm 3.0 3.1 3.3 3.5 3.7 3.8 3.9 Table 4 : 6/10KV, 1CORE Conductor Size mm2 25 35 50 70 95 120 150 185 240 300 Cable Type - RFOU, RFCU, RFOB, RFCB - CU, CB : with galvanized steel wire braid - OB, CB : Mud Resistant type Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.2 1.2 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 Diameter over inner covering mm 20.6 21.9 22.8 24.5 26.6 29.0 30.1 32.4 35.4 37.3 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 1160 1400 1520 1810 2160 2550 3100 3480 4280 5120 mm 1.7 1.8 1.8 1.9 2.0 2.0 2.1 2.2 2.3 2.4 mm 27.0 28.3 29.5 31.5 33.3 35.8 37.5 40.0 43.5 45.8 mm 1.6 1.7 1.7 1.8 2.0 2.1 2.2 2.4 2.6 2.7 Table 1 : 3.6/6KV, 1CORE Conductor Size mm2 25 35 50 70 95 120 150 185 240 300 Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.2 1.2 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 3.0 3.0 3.0 3.0 3.0 3.0 3.0 3.0 3.0 3.0 Diameter over inner covering mm 19.8 21.1 22.0 23.7 25.8 28.2 29.3 31.6 34.6 36.5 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 1070 1220 1400 1650 1980 2370 2570 3140 3970 4550 mm 1.7 1.7 1.8 1.8 1.9 2.0 2.1 2.2 2.3 2.4 mm 25.5 26.5 28.0 30.0 32.0 34.5 36.0 38.5 42.0 44.0 mm 1.5 1.6 1.7 1.8 1.9 2.1 2.2 2.3 2.5 2.7 Table 5 : 6/10KV, 3CORE Conductor Size mm2 25 35 50 70 95 120 Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 Inner covering thickness mm 1.4 1.4 1.4 1.6 1.6 1.6 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 mm 3.4 3.4 3.4 3.4 3.4 3.4 Diameter over inner covering mm 43.3 45.9 47.8 51.9 56.6 60.8 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 4300 4850 5600 6650 7950 9210 mm 2.6 2.7 2.8 3.0 3.2 3.3 mm 51.8 54.5 57.0 62.0 66.2 70.8 mm 3.1 3.3 3.4 3.5 3.5 3.7 H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 14 15 Marine & Offshore Cable

[close]

p. 9

Table 6 : 6/10KV, 3+E CORE Conductor Size mm2 25 35 50 70 95 120 150 B F O U BFCU BFOB BFCB Inner covering thickness mm 1.4 1.4 1.4 1.6 1.6 1.6 1.6 Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 mm 3.4 3.4 3.4 3.4 3.4 3.4 3.4 Diameter over inner covering mm 43.2 45.8 48.0 52.6 58.0 62.6 66.0 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 5100 5780 6700 8120 9950 11540 13420 NEK606 Type Cable Voltage rating - 3.6/6kV, 6/10kV, 8.7/15kV mm 2.6 2.7 2.8 3.0 3.2 3.4 3.5 mm 51.5 54.5 56.8 61.7 67.6 72.8 76.5 mm 3.0 3.1 3.2 3.5 3.7 3.8 3.9 Maximum conductor temperature - 85 Applied Standards - IEC 60092-354 - NEK 606 - IEC60331 - IEC 60332-3 Cat.AF - IEC 60754-1&2 - IEC 61034-2 Table 7 : 8.7/15KV, 1CORE Conductor Size mm2 35 50 70 95 120 150 185 240 300 Insulation thickness Dia. mm 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.2 1.2 1.2 1.2 1.2 1.4 Const. No./mm 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 4.5 4.5 4.5 4.5 4.5 4.5 4.5 4.5 4.5 Diameter over inner covering mm 23.9 25.1 26.9 29.2 30.9 32.5 34.7 37.4 40.1 Wire for braid mm 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 1510 1680 1950 2420 2850 3250 4560 4690 5430 Construction Details - Conductor IEC 60228 Class2 - Conductor Screen Semi-conducting compound - Fire proof layer Mica tape - Insulation HF-EPR as per IEC 60092-351 - Insulation Screen Semi-conducting compound - Metallic Screen Tinned copper wire braid or Tinned Copper tape - Inner covering Halogen-free compound - Armor Tinned copper wire braid - Sheath IEC 60092-359, SHF2 mm 1.8 1.9 1.9 2.0 2.1 2.2 2.3 2.4 2.5 mm 29.5 30.8 32.9 35.5 37.8 39.5 41.8 44.7 47.8 mm 1.8 1.8 2.0 2.1 2.3 2.4 2.5 2.7 2.9 Table 8 : 8.7/15KV, 3CORE Conductor Size mm2 25 35 50 70 95 120 Cable Type Insulation thickness Inner covering thickness mm 1.4 1.6 1.6 1.6 1.6 1.8 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 mm 4.5 4.5 4.5 4.5 4.5 4.5 Diameter over inner covering mm 47.7 50.8 53.5 57.4 61.7 65.6 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 3970 4570 5250 6150 7350 8500 - BFOU, BFCU, BFOB, BFCB - CU, CB : with galvanized steel wire braid - OB, CB : Mud Resistant type mm 2.8 2.9 3.0 3.2 3.4 3.5 mm 56.0 59.5 62.4 66.5 71.3 75.5 mm 3.4 3.6 3.7 4.0 4.3 4.5 Table 10 : 3.6/6KV, 1CORE Conductor Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Table 9 : 8.7/15KV, 3+E CORE Conductor Size mm2 25 35 50 70 95 120 150 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.2 1.2 1.2 Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 Inner covering thickness mm 1.4 1.6 1.6 1.6 1.6 1.8 1.8 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 mm 4.5 4.5 4.5 4.5 4.5 4.5 4.5 Diameter over inner covering mm 46.5 49.9 53.2 57.5 62.5 66.8 70.8 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 4220 4950 5640 6920 8450 9860 11350 Size mm2 25 35 50 70 95 120 150 185 240 300 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 3.0 3.0 3.0 3.0 3.0 3.0 3.0 3.0 3.0 3.0 Diameter over inner covering mm 21.4 22.7 23.6 25.3 27.9 29.8 30.9 33.2 36.2 38.5 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 1140 1290 1450 1780 2190 2530 2980 3510 4250 5000 mm 1.7 1.8 1.8 1.9 2.0 2.1 2.1 2.2 2.4 2.4 mm 26.5 28.0 29.0 31.0 34.0 36.0 38.0 40.0 43.5 46.0 mm 1.6 1.7 1.8 1.9 2.1 2.2 2.3 2.4 2.6 2.8 mm 2.7 2.9 3.0 3.2 3.4 3.6 3.7 mm 54.8 58.5 62.0 66.8 72.3 76.9 81.5 mm 3.3 3.5 3.7 4.0 4.3 4.6 4.9 H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 16 17 Marine & Offshore Cable

[close]

p. 10

Table 11 : 3.6/6KV, 3CORE Conductor Size mm2 25 35 50 70 95 120 150 Table 15 : 6/10kV, 3+E CORE Insulation thickness Inner covering thickness mm 1.4 1.4 1.6 1.6 1.6 1.6 1.6 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 mm 3.0 3.0 3.0 3.0 3.0 3.0 3.0 Diameter over inner covering mm 44.4 47.4 49.7 53.4 58.1 62.2 65.0 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 4070 4570 5300 6370 7730 9070 10400 Conductor Size mm2 25 35 50 70 95 120 150 Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 Inner covering thickness mm 1.4 1.6 1.6 1.6 1.6 1.8 1.8 mm 2.7 2.8 2.9 3.0 3.2 3.4 3.5 mm 52.0 55.0 58.0 62.0 67.0 71.0 75.0 mm 3.0 3.1 3.3 3.5 3.5 3.7 3.7 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 mm 3.4 3.4 3.4 3.4 3.4 3.4 3.4 Diameter over inner covering mm 46.6 50.0 52.3 56.5 62.0 66.7 70.0 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 5810 6620 7580 9010 11500 12600 14400 mm 2.8 2.9 3.0 3.2 3.4 3.6 3.7 mm 55.2 59.0 61.5 66.0 72.0 77.0 80.5 mm 3.3 3.4 3.5 3.8 3.9 4.0 4.0 Table 12 : 3.6/6KV, 3+E CORE Conductor Size mm2 25 35 50 70 95 120 150 Table 16 : 8.7/15KV, 1CORE Inner covering thickness mm 1.4 1.4 1.6 1.6 1.6 1.8 1.8 Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 mm 3.0 3.0 3.0 3.0 3.0 3.0 3.0 Diameter over inner covering mm 44.4 47.6 50.6 54.7 60.0 64.9 68.1 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 5300 6000 6880 8280 9980 11700 13400 Conductor Size mm2 35 50 70 95 120 150 185 240 300 Insulation thickness Dia. mm 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.2 1.2 1.2 1.2 1.2 1.4 1.4 mm 2.7 2.8 2.9 3.1 3.3 3.5 3.6 mm 52.9 56.3 59.0 63.5 69.5 75.0 78.0 mm 3.0 3.1 3.3 3.5 3.5 3.7 3.7 Const. No./mm 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 4.5 4.5 4.5 4.5 4.5 4.5 4.5 4.5 4.5 Diameter over inner covering mm 24.7 26.0 28.2 30.1 31.7 33.3 35.2 38.2 40.6 Wire for braid mm 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 1560 1730 2050 2520 3000 3400 4890 4760 5680 mm 1.9 1.9 2.0 2.1 2.2 2.2 2.3 2.4 2.5 mm 30.7 32.2 34.6 37.2 38.9 40.6 42.7 45.9 48.6 mm 1.8 1.9 2.1 2.2 2.3 2.4 2.6 2.8 2.9 Table 13 : 6/10KV, 1CORE Conductor Size mm2 25 35 50 70 95 120 150 185 240 300 Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.2 1.2 1.2 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 3.4 Diameter over inner covering mm 22.4 23.7 24.6 26.3 28.9 30.8 31.9 34.3 37.3 39.5 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 1250 1450 1700 1910 2330 2810 3150 3700 4420 5200 Table 17 : 8.7/15KV, 3CORE Conductor Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 mm 1.8 1.8 1.9 1.9 2.0 2.1 2.2 2.3 2.4 2.5 mm 28.5 29.8 30.8 32.7 35.5 38.2 39.5 42.0 45.0 47.5 mm 1.7 1.8 1.8 1.9 2.1 2.3 2.3 2.5 2.7 2.8 Inner covering thickness mm 1.6 1.6 1.6 1.6 1.8 1.8 Size mm2 25 35 50 70 95 120 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 mm 4.5 4.5 4.5 4.5 4.5 4.5 Diameter over inner covering mm 50.0 52.4 55.3 59.2 63.7 67.1 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 4120 4720 5550 6450 7800 8950 mm 2.9 3.0 3.1 3.3 3.4 3.6 mm 58.7 61.4 64.5 68.7 73.6 77.3 mm 3.5 3.7 3.9 4.1 4.4 4.6 Table 18 : 8.7/15KV, 3+E CORE Table 14 : 6/10KV, 3CORE Conductor Size mm2 25 35 50 70 95 120 Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 Inner covering thickness mm 1.4 1.6 1.6 1.6 1.6 1.6 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 mm 3.4 3.4 3.4 3.4 3.4 3.4 Diameter over inner covering mm 46.3 48.5 51.7 55.4 60.2 64.5 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Conductor Tolerance ( ) Approx. cable weight kg/km 4580 5240 5950 7050 8460 9980 Insulation thickness Dia. mm 6.42 7.56 8.9 10.7 12.6 14.21 15.75 Inner covering thickness mm 1.6 1.6 1.6 1.6 1.8 1.8 1.8 Size mm2 25 35 50 70 95 120 150 Const. No./mm 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 mm 4.5 4.5 4.5 4.5 4.5 4.5 4.5 Diameter over inner covering mm 52.0 54.4 57.3 61.2 65.7 69.1 72.4 Wire for braid mm 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 4370 5100 5940 7220 8900 10310 11800 mm 3.0 3.1 3.2 3.3 3.5 3.7 3.8 mm 60.9 63.5 66.7 70.9 75.7 79.5 83.1 mm 3.7 3.8 4.0 4.3 4.5 4.8 5.0 mm 2.8 2.8 3.0 3.1 3.3 3.5 mm 54.8 57.7 60.7 64.8 70.0 75.0 mm 3.3 3.5 3.5 3.6 3.8 3.9 H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 18 19 Marine & Offshore Cable

[close]

p. 11

Table 20 : 0.6/1KV, 2CORE R F O U RFCU RFOB RFCB NEK606 Type Cable Voltage rating - 0.6/1kV Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 Conductor Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.4 1.4 1.6 1.6 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 9.7 10.5 11.6 12.8 14.6 16.7 20.2 22.5 26.2 31.0 34.8 38.6 42.5 47.1 53.6 59.3 Wire for braid mm 0.2 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 332 460 541 634 803 1024 1410 1732 2223 3214 4034 4860 5784 6999 8872 10765 mm 1.3 1.3 1.4 1.4 1.5 1.6 1.7 1.8 1.9 2.2 2.3 2.5 2.6 2.8 3.1 3.3 mm 14.1 15.5 16.8 18.0 20.0 22.3 26.1 28.5 32.5 38.3 42.4 46.5 50.8 55.8 62.8 69.0 mm 0.7 0.8 0.8 0.9 1.0 1.1 1.3 1.4 1.6 1.9 2.1 2.3 2.5 2.8 3.1 3.4 Maximum conductor temperature - 85 Applied Standards - IEC 60092-353 - NEK 606 - IEC 60332-3 Cat.AF - IEC 60754-1&2 - IEC 61034-2 Construction Details - Conductor IEC 60228 Class2 - Insulation HF-EPR as per IEC 60092-351 - Inner covering Halogen-free compound - Armor Tinned copper wire braid - Sheath IEC 60092-359, SHF2 Table 21 : 0.6/1KV, 3CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.4 1.4 1.6 1.6 1.8 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 10.2 11.1 12.3 13.6 15.6 17.8 21.6 24.0 28.4 33.1 37.2 41.2 45.5 50.8 57.3 63.9 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 444 511 610 723 936 1215 1699 2115 2775 3951 5018 6079 7272 8916 11277 13837 mm 1.3 1.3 1.4 1.4 1.5 1.6 1.8 1.9 2.0 2.2 2.4 2.6 2.7 2.9 3.2 3.5 mm 15.2 16.2 17.5 18.9 21.0 23.5 27.5 30.2 34.9 40.6 45.0 49.4 54.0 59.8 66.8 73.9 mm 0.8 0.8 0.9 0.9 1.1 1.2 1.4 1.5 1.7 2.0 2.3 2.5 2.7 3.0 3.3 3.7 Cable Type - RFOU, RFCU, RFOB, RFCB - CU, CB : with galvanized steel wire braid - OB, CB : Mud Resistant type Table 19 : 0.6/1KV, 1CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 400 500 630 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 25.65 28.80 32.78 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.2 1.4 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 61/2.85 61/3.2 91/2.98 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 2.6 2.8 2.8 Diameter over inner covering mm 5.7 6.1 6.7 7.3 8.2 9.2 11.0 12.1 13.9 16.2 18.1 19.8 21.7 24.0 27.5 30.3 33.7 37.3 41.6 Wire for braid mm 0.2 0.2 0.2 0.2 0.2 0.2 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 182 203 235 270 337 423 661 796 993 1291 1616 1919 2274 2743 3481 4448 5050 5730 6620 Table 22 : 0.6/1KV, 4CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 mm 1.1 1.1 1.1 1.2 1.2 1.2 1.3 1.4 1.4 1.5 1.6 1.7 1.8 1.9 2.0 2.1 2.3 2.4 2.6 mm 9.8 10.2 10.8 11.5 12.5 13.6 16.0 17.3 19.3 21.7 23.7 25.6 27.7 30.2 33.9 37.5 41.2 45.1 49.8 mm 0.5 0.5 0.5 0.6 0.6 0.7 0.8 0.9 1.0 1.1 1.2 1.3 1.4 1.5 1.7 1.9 2.1 2.3 2.5 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.4 1.6 1.6 1.8 1.8 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 11.2 12.2 13.6 14.9 17.2 19.7 23.9 26.6 31.5 36.8 41.8 45.9 51.0 56.6 64.3 71.1 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 505 587 709 850 1116 1468 2077 2606 3646 4890 6313 7600 9191 11215 14325 17516 mm 1.3 1.4 1.4 1.5 1.6 1.7 1.8 2.0 2.2 2.4 2.6 2.7 3.0 3.2 3.5 3.8 mm 16.3 17.3 18.8 20.3 22.8 25.5 30.1 33.0 38.8 44.6 50.0 54.4 60.0 66.0 74.3 81.8 mm 0.8 0.9 0.9 1.0 1.1 1.3 1.5 1.7 1.9 2.2 2.5 2.7 3.0 3.3 3.7 4.1 H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 20 21 Marine & Offshore Cable

[close]

p. 12

Table 23 : 0.6/1KV, 2+E CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 Table 26 : 0.6/1KV, 1.5mm2 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.4 1.4 1.6 1.6 1.8 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 10.2 11.1 12.3 13.6 15.6 17.8 21.6 24.0 28.4 33.1 37.2 41.2 45.5 50.8 57.3 63.9 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 444 511 610 723 936 1215 1637 2044 2624 3728 4683 5711 6910 8297 10433 12749 No. of cores 2 4 7 9 12 14 19 23 27 33 37 44 Conductor Size mm2 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 mm 1.3 1.3 1.4 1.4 1.5 1.6 1.8 1.9 2.0 2.2 2.4 2.6 2.7 2.9 3.2 3.5 mm 15.2 16.2 17.5 18.9 21.0 23.5 27.5 30.2 34.9 40.6 45.0 49.4 54.0 59.8 66.8 73.9 mm 0.8 0.8 0.9 0.9 1.1 1.2 1.4 1.5 1.7 2.0 2.3 2.5 2.7 3.0 3.3 3.7 Const. No./mm 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 Dia. mm 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 Diameter Insulation Inner over thickness covering inner thickness covering mm mm mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 9.7 12.2 13.3 15.6 17.6 18.5 20.7 23.0 25.0 27.0 28.5 32.2 Wire for braid mm 0.2 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 Overall Tolerance Sheath thickness diameter ( ) Approx. cable weight kg/km 332 563 662 827 993 1085 1307 1539 1755 2011 2205 2885 mm 1.3 1.4 1.4 1.5 1.6 1.6 1.7 1.8 1.9 2.0 2.0 2.2 mm 14.1 17.4 18.6 21.1 23.2 24.3 26.6 29.1 31.2 33.4 35.0 39.6 mm 0.7 0.9 0.9 1.1 1.2 1.2 1.3 1.5 1.6 1.7 1.8 2.0 Table 27 : 0.6/1KV, 2.5mm2 No. of cores Conductor Size mm2 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 Table 24 : 0.6/1KV, 3+E CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.4 1.6 1.6 1.6 1.8 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 11.2 12.2 13.6 14.9 17.2 19.7 22.9 26.0 29.8 34.5 39.4 43.8 48.9 53.0 59.5 66.3 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 493 568 679 806 1042 1351 1747 2222 2761 3882 4966 6063 7429 8659 10828 13222 2 4 5 7 9 12 19 27 33 37 44 Const. No./mm 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 Dia. mm 2.01 2.01 2.01 2.01 2.01 2.01 2.01 2.01 2.01 2.01 2.01 Diameter Insulation Inner over thickness covering inner thickness covering mm mm mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.2 10.5 12.2 13.4 14.6 17.2 19.3 22.8 28.0 30.2 31.4 35.6 Wire for braid mm 0.2 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 Overall Tolerance Sheath thickness diameter ( ) Approx. cable weight kg/km 383 549 617 691 856 1010 1283 1742 2171 2306 2784 mm 1.3 1.4 1.4 1.5 1.6 1.7 1.8 2.0 2.1 2.2 2.3 mm 15.0 17.3 18.6 20.0 22.7 25.1 28.9 34.4 37.4 38.8 43.2 mm 0.7 0.9 0.9 1.0 1.1 1.3 1.4 1.7 1.9 1.9 2.2 mm 1.3 1.4 1.4 1.5 1.6 1.7 1.8 1.9 2.1 2.3 2.5 2.7 2.9 3.0 3.3 3.6 mm 16.3 17.3 18.8 20.3 22.8 25.5 29.0 32.4 36.4 42.0 47.4 52.1 57.7 62.2 69.2 76.5 mm 0.8 0.9 0.9 1.0 1.1 1.3 1.4 1.6 1.8 2.1 2.4 2.6 2.9 3.1 3.5 3.8 Table 25 : 0.6/1KV, 4+E CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.4 1.6 1.6 1.6 1.8 1.8 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 12.3 13.4 15.0 16.5 19.0 21.9 25.6 29.4 33.4 39.2 44.3 49.5 54.8 59.8 67.7 74.9 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 555 640 766 909 1173 1519 1981 2548 3371 4479 5643 6934 8400 9843 12405 15041 mm 1.4 1.4 1.5 1.6 1.7 1.8 1.9 2.1 2.2 2.5 2.7 2.9 3.1 3.3 3.6 3.9 mm 17.5 18.7 20.4 22.1 24.8 27.9 31.9 36.1 40.9 47.2 52.7 58.4 64.1 69.5 78.0 85.8 mm 0.9 0.9 1.0 1.1 1.2 1.4 1.6 1.8 2.0 2.4 2.6 2.9 3.2 3.5 3.9 4.3 H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 22 23 Marine & Offshore Cable

[close]

p. 13

Table 29 : 0.6/1KV, 2CORE B F O U BFCU BFOB BFCB NEK606 Type Cable Voltage rating - 0.6/1kV Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 Conductor Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.4 1.4 1.6 1.6 1.6 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 10.8 11.7 12.8 13.9 15.8 17.9 21.3 23.6 27.5 32.0 35.8 39.4 43.3 48.3 54.4 60.1 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 454 511 591 685 858 1083 1474 1800 2327 3292 4117 4935 5864 7149 8966 10866 mm 1.3 1.4 1.4 1.4 1.5 1.6 1.7 1.8 2.0 2.2 2.3 2.5 2.6 2.8 3.1 3.3 mm 15.9 16.8 18.0 19.2 21.2 23.5 27.3 29.7 34.0 39.4 43.5 47.4 51.6 57.1 63.7 69.8 mm 0.8 0.8 0.9 1.0 1.1 1.2 1.4 1.5 1.7 2.0 2.2 2.4 2.6 2.9 3.2 3.5 Maximum conductor temperature - 85 Applied Standards - IEC 60092-353 - NEK 606 - IEC60331 - IEC 60332-3 Cat.AF - IEC 60754-1&2 - IEC 61034-2 Construction Details - Conductor IEC60228 Class 2 - Fire proof layer Mica tape - Insulation HF-EPR as per IEC 60092-351 - Inner covering Halogen-free compound - Armor Tinned copper wire braid - Sheath IEC 60092-359, SHF2 Table 30 : 0.6/1KV, 3CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.4 1.4 1.6 1.6 1.8 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 11.5 12.4 13.5 14.8 16.8 19.0 22.8 25.2 29.4 34.2 38.7 42.1 46.3 51.7 58.2 64.7 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 495 563 661 776 991 1274 1763 2183 2839 4027 5154 6152 7349 9000 11367 13934 mm 1.4 1.4 1.4 1.5 1.6 1.7 1.8 1.9 2.1 2.3 2.5 2.6 2.8 3.0 3.2 3.5 mm 16.6 17.6 18.8 20.2 22.3 24.8 28.8 31.5 36.0 41.7 46.6 50.3 54.9 60.7 67.8 74.9 mm 0.8 0.9 0.9 1.0 1.1 1.2 1.4 1.6 1.8 2.1 2.3 2.5 2.7 3.0 3.4 3.7 Cable Type - BFOU, BFCU, BFOB, BFCB - CU, CB : with galvanized steel wire braid - OB, CB : Mud Resistant type Table 28 : 0.6/1KV, 1CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 400 500 630 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 25.65 28.80 32.78 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.4 1.4 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 61/2.85 61/3.2 91/2.98 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 2.6 2.8 2.8 Diameter over inner covering mm 6.3 6.7 7.2 7.8 8.7 9.8 11.5 12.7 14.4 16.7 18.6 20.2 22.1 24.4 27.9 30.7 34.1 38.1 42.1 Wire for braid mm 0.2 0.2 0.2 0.2 0.2 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 198 219 250 285 352 521 681 816 1011 1309 1635 1935 2291 2759 3499 4469 5550 6230 7030 Table 31 : 0.6/1KV, 4CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 mm 1.1 1.1 1.2 1.2 1.2 1.3 1.4 1.4 1.5 1.6 1.6 1.7 1.8 1.9 2.0 2.1 2.3 2.4 2.6 mm 10.4 10.9 11.5 12.1 13.1 14.8 16.6 17.9 19.8 22.2 24.3 26.0 28.1 30.6 34.3 38.0 41.7 46.0 50.3 mm 0.5 0.5 0.6 0.6 0.7 0.7 0.8 0.9 1.0 1.1 1.2 1.3 1.4 1.5 1.7 1.9 2.1 2.3 2.5 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.4 1.4 1.6 1.6 1.8 1.8 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 12.6 13.6 14.9 16.3 18.5 21.1 25.2 28.4 32.6 38.4 43.0 46.8 52.0 57.5 65.2 72.1 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 563 646 767 910 1179 1535 2150 2724 3726 5032 6407 7684 9281 11311 14430 17628 mm 1.4 1.4 1.5 1.5 1.6 1.7 1.9 2.0 2.2 2.4 2.6 2.8 3.0 3.2 3.5 3.8 mm 17.8 18.9 20.3 21.8 24.2 27.0 31.5 34.9 40.1 46.3 51.3 55.5 61.0 67.1 75.4 82.9 mm 0.9 0.9 1.0 1.1 1.2 1.3 1.6 1.7 2.0 2.3 2.6 2.8 3.1 3.4 3.8 4.1 H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 24 25 Marine & Offshore Cable

[close]

p. 14

Table 32 : 0.6/1KV, 2+E CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 Table 35 : 0.6/1KV, 1.5mm2 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.4 1.4 1.6 1.6 1.8 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 11.5 12.4 13.5 14.8 16.8 19.0 22.8 25.2 29.4 34.2 38.7 42.1 46.3 51.7 58.2 64.7 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 495 563 661 776 991 1274 1703 2113 2690 3807 4824 5785 6988 8383 10530 12854 No. of cores 2 4 5 7 9 12 14 19 23 27 33 37 44 Conductor Size mm2 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 mm 1.4 1.4 1.4 1.5 1.6 1.7 1.8 1.9 2.1 2.3 2.5 2.6 2.8 3.0 3.2 3.5 mm 16.6 17.6 18.8 20.2 22.3 24.8 28.8 31.5 36.0 41.7 46.6 50.3 54.9 60.7 67.8 74.9 mm 0.8 0.9 0.9 1.0 1.1 1.2 1.4 1.6 1.8 2.1 2.3 2.5 2.7 3.0 3.4 3.7 Const. No./mm 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 Dia. mm 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 Diameter Insulation Inner over thickness covering inner thickness covering mm mm mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.2 10.8 12.6 13.9 15.1 17.8 20.0 21.2 23.7 26.3 29.0 31.4 32.6 36.9 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 Overall Tolerance Sheath thickness diameter ( ) Approx. cable weight kg/km 454 563 637 734 924 1110 1210 1451 1713 1997 2491 2664 3226 mm 1.3 1.4 1.4 1.5 1.6 1.7 1.7 1.8 1.9 2.1 2.2 2.2 2.4 mm 15.9 17.8 19.2 20.5 23.4 25.9 27.1 29.8 32.7 35.6 38.7 40.1 44.7 mm 0.8 0.9 1.0 1.0 1.2 1.3 1.4 1.5 1.6 1.8 1.9 2.0 2.2 Table 36 : 0.6/1KV, 2.5mm2 No. of cores 2 4 5 7 9 12 14 19 23 27 33 37 44 Table 33 : 0.6/1KV, 3+E CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 Conductor Size mm2 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 2.5 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.4 1.4 1.6 1.6 1.6 1.8 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 12.6 13.6 14.9 16.3 18.5 21.1 24.3 27.8 31.0 35.7 40.6 44.8 49.9 54.1 60.5 67.2 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 556 633 743 873 1113 1427 1830 2351 3059 3985 5074 6165 7539 8776 10949 13354 Const. No./mm 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 7/0.67 Dia. mm 2.01 2.01 2.01 2.01 2.01 2.01 2.01 2.01 2.01 2.01 2.01 2.01 2.01 Diameter Insulation Inner over thickness covering inner thickness covering mm mm mm 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.2 1.4 11.7 13.6 15.0 16.4 19.3 21.8 23.0 25.8 29.1 31.6 34.2 35.6 40.7 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 Overall Tolerance Sheath thickness diameter ( ) Approx. cable weight kg/km 511 646 729 860 1090 1321 1448 1755 2123 2645 3022 3245 3995 mm 1.4 1.4 1.5 1.5 1.7 1.8 1.8 1.9 2.1 2.2 2.3 2.3 2.5 mm 16.8 18.9 20.4 21.9 25.1 27.8 29.1 32.1 35.7 38.9 41.7 43.3 48.8 mm 0.8 0.9 1.0 1.1 1.3 1.4 1.5 1.6 1.8 1.9 2.1 2.2 2.4 mm 1.4 1.4 1.5 1.5 1.6 1.7 1.9 2.0 2.1 2.3 2.5 2.7 2.9 3.1 3.3 3.6 mm 17.8 18.9 20.3 21.8 24.2 27.0 30.5 34.3 38.3 43.3 48.7 53.3 58.8 63.3 70.3 77.6 mm 0.9 0.9 1.0 1.1 1.2 1.3 1.5 1.7 1.9 2.2 2.4 2.7 2.9 3.2 3.5 3.9 Table 34 : 0.6/1KV, 4+E CORE Conductor Size mm2 1.5 2.5 4 6 10 16 25 35 50 70 95 120 150 185 240 300 Insulation thickness Dia. mm 1.59 2.01 2.55 3.12 4.05 5.1 6.42 7.56 8.9 10.7 12.6 14.21 15.75 17.64 20.25 22.68 Inner covering thickness mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.4 1.4 1.6 1.6 1.6 1.8 1.8 Const. No./mm 7/0.53 7/0.67 7/0.85 7/1.04 7/1.35 7/1.7 7/2.14 7/2.52 19/1.78 19/2.14 19/2.52 37/2.03 37/2.25 37/2.52 61/2.25 61/2.52 mm 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 1.6 1.6 1.8 2.0 2.2 2.4 Diameter over inner covering mm 13.9 15.0 16.5 18.0 20.6 23.4 27.5 30.9 34.8 40.6 45.6 50.7 56.0 60.9 68.8 76.0 Wire for braid mm 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.4 0.4 0.4 0.4 0.4 0.4 0.4 Sheath thickness Overall diameter Tolerance ( ) Approx. cable weight kg/km 632 721 846 992 1263 1616 2128 2876 3493 4616 5787 7069 8546 9998 12571 15221 mm 1.4 1.5 1.6 1.6 1.7 1.8 2.0 2.1 2.3 2.5 2.7 2.9 3.1 3.3 3.7 3.9 mm 19.2 20.5 22.0 23.7 26.4 29.5 34.0 38.2 42.4 48.7 54.1 59.6 65.3 70.7 79.2 87.0 mm 1.0 1.0 1.1 1.2 1.3 1.5 1.7 1.9 2.1 2.4 2.7 3.0 3.3 3.5 4.0 4.4 H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 26 27 Marine & Offshore Cable

[close]

p. 15

RFOU(c) RFCU(c) RFOB(c) RFCB(c) NEK606 Type Cable Voltage rating - 250V Table 38 : 250V, 1mm2 No. of pairs/ triads 1P 2P 3P 4P 5P 7P 8P 10P 12P 16P 20P 24P 32P 1T 2T 4T 8T 12T 16T 24T 32T Conductor Size mm2 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 Const. No./mm 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 7/0.43 Dia. mm 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 1.29 Diameter Insulation Inner over thickness covering inner thickness covering mm mm mm 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.4 8.3 12.7 13.5 14.8 16.6 17.2 19.0 21.6 22.5 25.5 26.7 31.0 33.6 8.7 14.7 17.2 22.8 28.4 31.8 40.2 44.5 Wire for braid mm 0.2 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.2 0.3 0.3 0.3 0.3 0.4 0.4 0.4 Overall Tolerance Sheath thickness diameter ( ) Approx. cable weight kg/km 277 585 646 741 872 944 1070 1322 1426 1745 1917 2613 3044 303 717 930 1446 2046 2702 3933 4726 mm 1.2 1.4 1.4 1.5 1.6 1.6 1.7 1.8 1.8 1.9 2.0 2.1 2.3 1.2 1.5 1.6 1.8 2.0 2.2 2.5 2.7 mm 12.6 18.0 18.8 20.2 22.1 22.8 24.7 27.6 28.6 31.8 33.1 38.2 41.1 13.1 20.1 22.8 28.8 34.9 39.1 48.3 52.9 mm 0.6 0.9 0.9 1.0 1.1 1.1 1.2 1.4 1.4 1.6 1.7 1.9 2.1 0.7 1.0 1.1 1.4 1.7 2.0 2.4 2.6 Maximum conductor temperature - 85 Applied Standards - IEC 60092-3 - NEK 606 - IEC 60332-3 Cat. AF - IEC 60754-1&2 - IEC 61034-2 Construction Details - Conductor IEC 60228 Class 2 - Insulation HF-EPR as per IEC 60092-351 - Collective screen Copper or aluminum backed polyester tape with tinned copper drain wire - Inner covering Halogen-free compound - Armor Tinned copper wire braid - Sheath IEC 60092-359, SHF2 Table 39 : 250V, 1.5mm2 No. of pairs/ triads 1P 2P 3P 4P 5P 7P 8P 10P 12P 16P 20P 24P 32P 1T 2T 4T 8T 12T 16T 24T 32T Conductor Size mm2 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 1.5 Cable Type - RFOU(c), RFCU(c), RFOB(c), RFCB(c) - CU, CB : with galvanized steel wire braid - OB, CB : Mud Resistant type Const. No./mm 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 7/0.53 Dia. mm 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 1.59 Diameter Insulation Inner over thickness covering inner thickness covering mm mm mm 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.2 1.2 1.0 1.0 1.0 1.0 1.2 1.2 1.4 1.6 8.9 13.8 14.6 16.1 18.0 18.7 20.7 23.6 24.6 28.2 29.6 33.8 36.8 9.4 15.9 18.7 24.8 30.9 34.6 43.9 49.0 Wire for braid mm 0.2 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.4 0.2 0.3 0.3 0.3 0.4 0.4 0.4 0.4 Overall Tolerance Sheath thickness diameter ( ) Approx. cable weight kg/km 311 664 740 855 1013 1107 1254 1564 1696 2131 2355 3127 3674 341 819 1081 1713 2653 3224 4724 5785 mm 1.2 1.4 1.5 1.5 1.6 1.6 1.7 1.8 1.9 2.0 2.1 2.3 2.4 1.2 1.5 1.6 1.9 2.1 2.3 2.7 2.9 mm 13.2 19.1 20.0 21.6 23.7 24.4 26.5 29.7 30.8 34.8 36.2 41.3 44.5 13.8 21.4 24.4 31.0 38.2 42.2 52.2 57.8 mm 0.7 1.0 1.0 1.1 1.2 1.2 1.3 1.5 1.5 1.7 1.8 2.1 2.2 0.7 1.1 1.2 1.6 1.9 2.1 2.6 2.9 Table 37 : 250V, 0.75mm2 No. of pairs/ triads 1P 2P 3P 4P 5P 7P 8P 10P 12P 16P 20P 24P 32P 1T 2T 4T 8T 12T 16T 24T 32T Conductor Size mm2 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 0.75 Const. No./mm 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 7/0.37 Dia. mm 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 1.11 Diameter Insulation Inner over thickness covering inner thickness covering mm mm mm 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 0.8 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.0 1.2 1.2 1.0 1.0 1.0 1.0 1.0 1.2 1.4 1.4 7.9 12.1 12.8 14.1 15.7 16.3 18.0 20.5 21.3 24.1 25.2 29.2 31.8 8.3 14.0 16.3 21.6 26.4 30.0 38.0 42.0 Wire for braid mm 0.2 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.3 0.4 0.2 0.3 0.3 0.3 0.3 0.4 0.4 0.4 Overall Tolerance Sheath thickness diameter ( ) Approx. cable weight kg/km 259 542 595 679 796 856 970 1191 1281 1559 1705 2134 2703 282 661 847 1300 1791 2418 3502 4188 mm 1.2 1.4 1.4 1.5 1.5 1.5 1.6 1.7 1.7 1.9 1.9 2.1 2.2 1.2 1.4 1.5 1.8 1.9 2.1 2.4 2.6 mm 12.2 17.3 18.1 19.4 21.2 21.8 23.6 26.3 27.3 30.3 31.5 35.9 39.1 12.6 19.3 21.9 27.5 32.8 37.2 45.9 50.3 mm 0.6 0.9 0.9 1.0 1.1 1.1 1.2 1.3 1.4 1.5 1.6 1.8 2.0 0.6 1.0 1.1 1.4 1.6 1.9 2.3 2.5 H Marine & Offshore Cable a l o g e n F r e e a n d M u d R e s i s t a n t C a b l e 28 29 Marine & Offshore Cable

[close]